[Steam-engine] boiler feedwater injector conection
Blake
blake at little-mountain.com
Mon Nov 7 23:30:58 PST 2005
I tried to answer some questions yesterday, but the email didn't
go through.
As far as a feed water line into the vertical boiler under
discussion, I would not run it into the bottom as it would stir up
the sludge as water is put in. I would run it into the top of the
boiler, but I would put a pipe inside the boiler to a point well
below the water level, but not too close to the tube sheet.
As far as whether to keep dissolved solids and sludge
(precipitated junk) in suspension, or let it settle out - I would
say definately let it settle out so it can be blown out with the
blowdown valve. Dissolved solids in the water will continue to
build up as more impure water is introduced and clean water is
evaporated as steam. The dissolved solids will cause high
conductivity, scaling of the tubes, priming, and a bunch of bad
things. You have to get rid of it. There are standards as to how
much blowdown there should be in relation to how much water is fed
to the boiler. A surface blowdown is good too as it will remove
lighter stuff that does not settle out. Bottom blowdown should be
opened wide at least once a day with full steam pressure.
If you can check conductivity of your boiler water, we try to keep
it around 5000 microhms at work. Conductivity will basically tell
you the amount of dissolved solids in your water.
For the feed water lines, use a cross if you can as they give full
access to both directions for cleaning and inspecting.
Blake
Conneautville, Pa.
On Sun Nov 06 15:22:01 PST 2005, Jeff Smith
<steamenginesmitty at yahoo.com> wrote:
> Ken,
>
> I will agree with you on the use of a tee in that
> location, and I am even considering doing that in a
> few other locations. I have even been told that the
> code in Canada requires many areas to be plumbed like
> that, but maybe someone could shed some more light on
> that?
>
> Jeff Smith
>
> --- Ken Majeski <fuller_johnson1 at msn.com> wrote:
>
>> Well as long as were talking about feedwater iI
>> would like to mention something... I see many boilers at shows
>> where the
>> feedwater is piped to a elbow at the boiler. You should always
>> use a T or a
>> cross there as that way you can take out the plug and inspect
>> and clean the
>> nipple as in hard water they can lime up pretty quickly. Also it
>> will allow
>> you to keep tabs on the pipe condition there.
>>
>> I mention this to the people with the engines and
>> they look at you like your talking Greek or something...???
>>
>>
>>
>> Ken Majeski, Ellsworth Wis. Case Steam Engine, Rumely Oilpulls
>> H, F, & R. Website, Http://www.pressenter.com/~kmajeski/
>
>
>
>