Excellent question Charlie, the short answer is in an ideal world if the GFCI
is not connected to earth, you can't get a shock and so the GFCI does
nothing. Sometimes the world is not ideal, and something gets connected to
the earth, and then the GFCI protects you.
There are two different things we mean by ground. One it an actual
connection to the Earth, and the other is the ground wires run all over your
house. I did not specify (and in fact rarely does anyone specify), but the
two are very different. We don't think of them as difference because the
ground wires are normally (but not always!) connected to the earth at some
point.
Power comes always comes in 2 sides. We say hot and neutral, but in truth,
both wires are equally hot - the only difference is one wire is connected to
the ground wires (which are normally connected to the earth), and the other
is not. We call this hot wire neutral, but there is no significant
difference (note that your house is 220, and there is a difference, but not
in any way that is important to this discussion so I'm going to ignore that
case to avoid confusion).
For electric current to flow there must be a connection between the two hot
wires. If there is no connection no current flows. If there is no earth
connection and you grab a hot wire nothing happens - you don't get a shock
because there is no way for power to get between you and the other hot wire.
Connect one wire to a ground rod though, and grab the other and you will get
a shock because current can flow through you, through the ground, and back to
the other wire.
If you understood the above you will now be asking "Why do they have ground
rods if they just make electric shock possible?" The reason is the real
world is messier, and an ungrounded system can burn your house down in some
situations where a ground would not. If a mouse chews on the wires in your
walls (which happens all the time), you can have a bare wire providing a poor
earth connection. If a second mouse chews the the other wire elsewhere, a
small amount of current can flow - not enough to blow fuses, but plenty to
start a fire in the walls. By adding a ground wire and earth connection
odds are much better that enough current will flow to blow a fuse long before
a fire can start if there is a problem.
As you see, the earth/ground system is for fire protection, not human safety.
So if your generator is not earthed, why the GFCI? The problem is you cannot
be sure that the entire system isn't earthed. An internal problem may
connect one wire to the frame, which touches the earth. Now you have a
grounded system. A GFCI will protect you from trouble now, just like it
will in hour house.
Note that a GFCI does NOT require a ground/earth connect. The GFCI just
measures the current in the two hot wires. If there is any difference, the
rest of the current must be getting back some other way - by which it assumes
the earth via your body, so trips to protect you. Code allows (as in
strongly discouraged but sometimes there is no choice) a GFCI protected
outlet to have a ground terminal that is not connected to anything.
So I say use a GFCI outlet on your portable power generators because they will
protect you in case something is wrong. There is a small possibility that
something could go wrong and cause a fire, but since this is a portable
power, you should be right there to see problems before they become big.
When connected to your house, use the house's ground/earth system for fire
safety.
On Sunday 16 December 2007 19:57:01 charlie hill wrote:
> Henry, I've already admitted that I'm no electrician but I have to
> question one thing you are saying. How is a ground fault interupter going
> to work if it's not connected to a ground? If you are using any sort of
> tool that has a three prong plug and you don't have an earth ground on the
> generator YOU are going to become the ground if something goes wrong inside
> the tool.