I hope the following little table showing Load, Circuit Breaker and Wire
Size transmits in a readable fashion -
I took it from the NEC (National Electrical Code) probably 25 years ago but
I can't imagine it has changed.
Dudley Rupert
Snohomish, Washington
Load Circuit Breaker Wire Size
=<15 amps 15 amp Not less than #14
=<20 amps 20 amp Not less than #12
=<30 amps 30 amp Not less than #10
=<40 amps 40 amp Not less than #8
=<50 amps 50 amp Not less than #6
-----Original Message-----
From: at-bounces at lists.antique-tractor.com
[mailto:at-bounces at lists.antique-tractor.com]On Behalf Of John Wilkens
Sent: Tuesday, December 07, 2004 8:02 PM
To: at at lists.antique-tractor.com
Subject: [AT] Wire size for welder?? Help welder people!
If I have a 230 volt mig welder that is rated at 45 amps input current I
assume I would want a 50 amp 230 volt breaker . But what minimum romex
wire gauge would I need to run 25' from the breaker box to the outlet box
for the welder? For years I've used 10 gauge wire for my 225 amp output
Lincoln buzz box. John W.