If I have a 230 volt mig welder that is rated at 45 amps input current I
assume I would want a 50 amp 230 volt breaker . But what minimum romex
wire gauge would I need to run 25' from the breaker box to the outlet box
for the welder? For years I've used 10 gauge wire for my 225 amp output
Lincoln buzz box. John W.
In the wide-open spaces of NE Oregon
John:
#6 would handle that very well..... #6 copper. I have run farther than
that with a #8, but if you gotta get the wore anyway, #6 would be much better..
Cecil in OKla